Right. . i'm not a spark, never said I was, I have the basic knowledge of electrics. I haven't come on here to be ripped apart, just for some info & help (which is what I thought forums were for) and yes I may not of explained it correctly, but all the info is here.
My friend who i a spark, wired up the CU, I wired up the hob, when I switched on the hob at the cooker socket, it tripped the RCD on the CU. . got me so far? I always check the live with a volt tester, before and after switching off, when the RCD had tripped the live and the neutral were LIVE, I don't know why and yes my tester was lit up showing there was current to the live and the neutral. . oh and the neutral bar (the side the hob N was connected) in the CU was also showing live. Thats why I came on here as I had no idea and my mate wasn't answering the phone. So as already said, I went back to the start to work out what was going on, I was more worried that the cable I had run through the old ceiling had been damaged which would mean running a new one through a brand new plastered celling. . anyway, I saw that the neutral had been connected to the wrong side at the CU, and again, not being a spark, I still thought this could be the problem, so I moved the N over to the correct bar and its all working fine. So please don't always doubt people using forums. This wasn't a wind up nor am I a loser looking for banter or wind-ups online.
So thank you to those who gave advice and have helped made forums what they were put in place for.
Oh and i've made sure I have spell checked this, in case I get pulled on that also