sjm

Hi guys quick question.

I've got to supply a couple of static caravans from 32 amp hook ups. Can I use black HO7 flex or must it be blue artic?
Would 4.0mm (32 amp CCC) be ok, length of supply cable max 6mts, or should I move up to 6.0mm.

Thanks in advance.
Steve
 
The cable capacity, including rating/derating factors must be higher or equal to the circuit protection, and must be suitable for its environment.Who knows but you what conditions it is likely to face? Section 708 and 721 would apply.721.521.2 would apply, certainly inside, you need BS EN 60332-1-2 ....721.55.2.6 says you need BS7919 cable, and the CSA in the table shows a 6mm csa cable required....(Note that these are minimum requirements, if it is likely to be hit by a mower or passing vehicles etc, then it must have machanical protection, and any other hazard needs to be accounted for)Youi are on the ground, so no-one else can advise you without any more specific info.
 
Last edited by a moderator: