Agreed. Has the penny dropped that this presents a problem?I know we all make mistakes. I’ve learnt from it. Every day is a school day as the saying goes. If designing the circuit the CCC Table 4D2A
3 core in conduit is 27 amps in Conduit and 32 amps Clipped Direct.
If the cable is at risk of starting to melt above 27 amps loading, is a 40 amp MCB of any help to avoid this scenario?