By Marconi I have enjoyed pondering this problem but you no doubt might be frustrated with it. It is not completely clear to me whether you are simply taking continuity measurements on unconnected lengths of cable runs or end-to end on a growing length of cable run as you wire in the CRs. So I have assumed the former but what I am about to write applies to the latter as well.
A digital multi-meter, when set to measure resistance, does so by injecting a constant current through the circuit under test and then measuring the voltage across the circuit. Using Ohm's Law it then calculates the resistance of the current's path. As the resistance of the circuit under test increases, the injected constant current is reduced. This is because the DMM is both battery powered and for safety the applied voltage is limited to around 10 Volts. With the meter you are using the resistance scale is automatically changing up or down, so in turn is the injected constant current. By choosing the inject current to be 1, 0.1, 0.001 mA etcetera for example a straight voltage reading is the same numerical value as resistance for an applied emf of 10Volt - 10k, 100k, 1000k Ohms etcetera
Now let us think about your test arrangement. You are using one short test lead and one long wandering lead. These are connected to the part of the lighting radial circuit you want to test for continuity. These long leads form an aerial and which will pick up electro-magnetic radiation. A small alternating current will flow - micro-Amps - but comparable to the injected current on its higher resistance scales.
There are inevitable capacitance effects which albeit small need charging and discharging. Since the injected current is small on the higher range scales there is a settling time before reliable measurements may be taken.
The connections you make for a test - using your crocodile clips, test lead plugs, bared conductors , dirt- may be covered in grease, dirt, dust and oxidation. Not only do these act as resistive layers, they can also act in a non-linear way akin to a diode. (Railway signalling systems using the track and train wheels suffer from this especially in autumn). This is another interference mechanism to the injection current especially at higher resistance scales.
Before a current - a flow of electrons - can take place between metallic surfaces the so-called wetting current must be exceeded. For switch contacts carrying small currents a capacitor is sometimes connected across them which is discharged when they close to boost the wetting current.
There are then a number of electrical effects which make the DMM unreliable in your test rig when operating on the higher resistance scales. I suggest you only use the DMM for continuity and select an instrument with a higher applied voltage and current to measure higher resistance ; I do not know if the MFT does but the earlier poster recommends its use.
I hope this helps.
A digital multi-meter, when set to measure resistance, does so by injecting a constant current through the circuit under test and then measuring the voltage across the circuit. Using Ohm's Law it then calculates the resistance of the current's path. As the resistance of the circuit under test increases, the injected constant current is reduced. This is because the DMM is both battery powered and for safety the applied voltage is limited to around 10 Volts. With the meter you are using the resistance scale is automatically changing up or down, so in turn is the injected constant current. By choosing the inject current to be 1, 0.1, 0.001 mA etcetera for example a straight voltage reading is the same numerical value as resistance for an applied emf of 10Volt - 10k, 100k, 1000k Ohms etcetera
Now let us think about your test arrangement. You are using one short test lead and one long wandering lead. These are connected to the part of the lighting radial circuit you want to test for continuity. These long leads form an aerial and which will pick up electro-magnetic radiation. A small alternating current will flow - micro-Amps - but comparable to the injected current on its higher resistance scales.
There are inevitable capacitance effects which albeit small need charging and discharging. Since the injected current is small on the higher range scales there is a settling time before reliable measurements may be taken.
The connections you make for a test - using your crocodile clips, test lead plugs, bared conductors , dirt- may be covered in grease, dirt, dust and oxidation. Not only do these act as resistive layers, they can also act in a non-linear way akin to a diode. (Railway signalling systems using the track and train wheels suffer from this especially in autumn). This is another interference mechanism to the injection current especially at higher resistance scales.
Before a current - a flow of electrons - can take place between metallic surfaces the so-called wetting current must be exceeded. For switch contacts carrying small currents a capacitor is sometimes connected across them which is discharged when they close to boost the wetting current.
There are then a number of electrical effects which make the DMM unreliable in your test rig when operating on the higher resistance scales. I suggest you only use the DMM for continuity and select an instrument with a higher applied voltage and current to measure higher resistance ; I do not know if the MFT does but the earlier poster recommends its use.
I hope this helps.