mayfair

Hi
as most of you know I work in Spain as a sparky and have done for 20 years and as my Certs C&G are dated 1979 dont feel very qualified to answer a question that a very keen young lad has put to me! The Lad helps me out now and again and is off to the UK in September to start his C&G courses.
Right he has bought from e bay a insulation tester (Alphatek 1601) its in really good condition (For 35 quid) but the ranges are 250V 4000M ohm 500V 4000M ohm 1000V 4000M ohm. its seems to work did a quickie on a new install today for him the test comes up 4500M ohm is this meter gonna be accepted in the UK He has watched all the videos on Youtube etc and he tells me that none of the meters used seem to have these ranges.
He's only a young lad starting out and not much money ..........but he is trying to build up gear to help him practice on .................Whats ya verdict:)
 
the voltage ranges are the same. as long --- it measures Mohms . willprobsblyhave to get it calibrated in UK
 
Hi m8 it was calibrated last 2009 by MTI uk so he's only practising. He just reckons on the videos it says about filling in forms and it always refers to > 299 will he be alright putting down 4500 M ohm's I will have to see these videos he's got i suppose learning room or summit
 
Last edited by a moderator:
Hi m8 it was calibrated last 2009 by MTI uk so he's only practising. He just reckons on the videos it says about filling in forms and it always refers to > 299 will he be alright putting down 4500 M ohm's I will have to see these videos he's got i suppose learning room or summit

The >299 just refers to the maximum value the instrument will display. So if his instrument shows 4500Meg, and that is what he records then thats fine. Mine goes to 500meg, Metrel go to 1000meg. So if mine reaches 500 thats what i put. As long as it is greater then 0.5meg or 1 meg as required then all is well anyway.

Cheers.........Howard
 
Yep it's fine in fact it's damn good! Only thing is he'll almost certainly have to record result every time, rather than just wrtiting '>200' if the thing doesn't beep!
 
no problem with entering > 199M if the meter shows any reading above this. be it 200m or 4000M. what did we put down before all these fancy digital meters? my old megger ( analogue ) went to 5M then infinity.
 