i can't see anything amiss. hang on.uncertain of the labelling. which are the E-stops?
 
as in the upside down E's. so the e stops and start buttons are in the neutral then.
 
Also figure 7 looks as if it has a fused neutral! Hopefully it is really meaning an isolation link operated together with the live fuse, or a double-pole MCB.
 
Missed that! Although my own spelling is p-poor without the aid of the spell checker so not usually going to be the one throwing stones...
 
If it is for this machine from India it looks like they haven't changed the configuration from three phase to single. @darkwood would know whether the method of switching the neutral is acceptable but it could be reconfigured like this.20200412_121701.jpg
 
Switching the neutral is OK for lighting control circuits under 463.1.2 but no idea if there is a similar exception for other control circuits.
 
Last edited by a moderator:
Switching the neutral is very bad practice as any earth fault on the wiring after the stop button means the contactor will not de-energise when the stop button is pressed and no fuse will blow as it would be a neutral earth fault.
 
As the schematic is shown I would definately say it is wrong, the fuses themselves FU1 represent external fusing before the DOL starter, I contacted Chint UK technical on this matter pointing out what I see as an error, he suggested/stated it was a DP breaker and thus complied but my issue was this was not integral to the DOL starter so should not be shown as such and also the symbol is not a standard representative of a MCB and in fact would suggest it was individually fused contravening our regulations.
The fuses been external and on the power supply side means this falls under the BS7671 and not the BS60204 which is a little more complex and can often be confusing with control fusing to those not familiar with control circuits.

The technical support said he would raise my concerns internally although his comment that this was a global issued schematic didn't bode well as this is a schematic supplied with the product and sold into the UK market, this means it should meet UK standards and the literature also should show compliance which in this case the literature doesn't in my opinion.

A standard practice as you may expect would be to show only the ph1 line fused and the N uninterrupted which would be the normal practice of protecting the circuit supply.
 
Last edited:
As the schematic is shown I would definately say it is wrong, the fuses themselves FU1 represent external fusing before the DOL starter, I contacted Chint UK technical on this matter pointing out what I see as an error, he suggested/stated it was a DP breaker and thus complied but my issue was this was not integral to the DOL starter so should not be shown as such and also the symbol is not a standard representative of a MCB and in fact would suggest it was individually fused contravening our regulations.
The fuses been external and on the power supply side means this falls under the BS7671 and not the BS60204 which is a little more complex and can often be confusing with control fusing to those not familiar with control circuits.

The technical support said he would raise my concerns internally although his comment that this was a global issued schematic didn't bode well as this is a schematic supplied with the product and sold into the UK market, this means it should meet UK standards and the literature also should show compliance which in this case the literature doesn't in my opinion.

A standard practice as you may expect would be to show only the ph1 line fused and the N uninterrupted which would be the normal practice of protecting the circuit supply.
Thanks for that information, I definitely would not connect it the wY it’s shown in their diagram.
Agree on your intake Neutral uninterrupted & not used in the control circuits,onLG fo coil 230 v,
 

Reply to Am I missing something in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, agricultural off grid project, Victron inverter/charger, BYD LVS and Pramac GBW22P generator. The generator has a DSE4520 controller...
Replies
0
Views
195
Good day to you. I need electrical drawings urgently and hopefully there is someone that can assist me. They are all for electrical trade test...
Replies
6
Views
777
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
1K
Hi all, Thank you in advance... So I had an electrician put in some FCUs on spurs to a couple of outside lights.. this one was in readiness to...
Replies
17
Views
595
Would any fellow electricians consider using an open PEN device to protect a metal trailer used as a "Canteen". It is likely to be often connected...
Replies
3
Views
229

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock