resitting Saturday my am2 4 sections a3/b/d/e
swa and sy failed on protective conductors on both
swa i under stand thats the earths i think i used a smaller fly lead from the banjo to the db/ and a earthing nut with the banjo
sy think i used a 1.5mm flylead
so correct me if im wrong
the earth has to be the same size or bigger than the swa core size yellow lug
using the earthing nut no banjo required
 
in the day of 2c cable we used the same size earth fly lead as the line cores never bothered to work it out
 
Upvote 0

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

daza18

Trainee
Joined
Location
essex
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
am2 resit tommorrow swa/ sy earthing
Prefix
N/A
Forum
Electrician Courses : Electrical Quals
Start date
Last reply date
Replies
1
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
daza18,
Last reply from
Dustydazzler,
Replies
1
Views
2,100

Advert

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.