Tanzy

Evening all,

I'm currently doing a re-wire on a property and this is the state of the electrics. I think the property was last wired in the 40's.

Has anyone dealer with anything like this before. Any tips on disconnecting it??


Many Thanks
Tanzy
 
image.jpg

Sorry forgot to attach
 
just isolate as you would any other? theres a service fuse and old elcb or get dno to fit isolator, if its to be rewired cant see the issue.
 
True true how difficult are the DNO to get hold of to put a isolate switch in after the meter?? And who do I need to speak to about cutting the meter tailles to get access to change the meter tails.
 
True true how difficult are the DNO to get hold of to put a isolate switch in after the meter?? And who do I need to speak to about cutting the meter tailles to get access to change the meter tails.

As easy as calling anyone else! You may as well fit the isolator yourself if you want to get the job done quickly! ;)
 
turn the voelcb off. replace with 100A D/P isolator onto existing meter tails (live). then new CU and rewire circuits if required.
 
If the service fuse only has a seal on the bottom then 9 times out of 10 it can be removed without damaging the seal. Then carry on and do what Tel is advising ^^^^
 
is the VOELCB a crabtree....or a tenby?......put your ear up close to it......should give the game away....
 
Be handy if you could get hold of some kind of TN system, done some jobs around the Tavy area and a decent loop with a TT is non existant :lol:

Are those old MEM boxes fused neutral as well?
 
Why touch the fuse at all ...........use the VOELCB as your isolator and keep it.

It looks like it doesn't work anyways as the Earthing conductor is coming into the bottom of the unit and there is nothing in the top, the Zs readings in this installation is worth looking at.
 