hi guys
ive got myself a little confused here when trying to calculate a max demand figure for the installation below.
60amp TNCS supply to a bungalow.
1x 30A Ring Main
1x 30A cooker unit(with socket)
1x 40A Shower (8.5kw)
2x 20A Radials
1x 5A Lights (7x100w)
using table 1B app 1 OSG
ring main (30a) no diversity = 30A
cooker unit(30a) 10A+30%(fl)+5A =24A
shower(40a) no diversity = 36.9A
radial(20a) 40% = 8A
radial(20a) 40% = 8A
lights 66% =3.04A
using these figures it comes out at a diversified current of 109.9Amps what am i forgeting as this cant be right can it? do i have to apply diversity to the diversified currents
when i use my usual method of adding up the MCB's and then multiplying by 0.4
40+30+30+20+20+5 x 0.4 = 58 Amps
which is what id expect. any help would be appreciated.
hi guys
ive got myself a little confused here when trying to calculate a max demand figure for the installation below.
60amp TNCS supply to a bungalow.
1x 30A Ring Main
1x 30A cooker unit(with socket)
1x 40A Shower (8.5kw)
2x 20A Radials
1x 5A Lights (7x100w)
using table 1B app 1 OSG
ring main (30a) no diversity = 30A
cooker unit(30a) 10A+30%(fl)+5A =24A
shower(40a) no diversity = 36.9A
radial(20a) 40% = 8A
radial(20a) 40% = 8A
lights 66% =3.04A
using these figures it comes out at a diversified current of 109.9Amps what am i forgeting as this cant be right can it? do i have to apply diversity to the diversified currents
when i use my usual method of adding up the MCB's and then multiplying by 0.4
40+30+30+20+20+5 x 0.4 = 58 Amps
which is what id expect. any help would be appreciated.
And always come up with a totally unrealistic end figure!! lol!!!
Overcompensation it may be.
But I would rather go with the guidance and instruction of the nationally recognised productions in the court of law than guess work.
Overcompensation, ....that has to be the understatement of the year!!
Come on Widdler, we both know that the criteria within BS 7671 and it's guide doesn't work and come to that has never worked!! I have never seen or known of a single Electrical Design Engineer/Consultant etc, ever use them either!!!
You may need to support and use them as a collage lecturer, ...but they are going to be of little use to anyone outside that collage classroom...
i give up, i'm done with this!