ianphilip007

hi guys

ive got myself a little confused here when trying to calculate a max demand figure for the installation below.

60amp TNCS supply to a bungalow.

1x 30A Ring Main
1x 30A cooker unit(with socket)
1x 40A Shower (8.5kw)
2x 20A Radials
1x 5A Lights (7x100w)

using table 1B app 1 OSG

ring main (30a) no diversity = 30A
cooker unit(30a) 10A+30%(fl)+5A =24A
shower(40a) no diversity = 36.9A
radial(20a) 40% = 8A
radial(20a) 40% = 8A
lights 66% =3.04A

using these figures it comes out at a diversified current of 109.9Amps what am i forgeting as this cant be right can it? do i have to apply diversity to the diversified currents

when i use my usual method of adding up the MCB's and then multiplying by 0.4

40+30+30+20+20+5 x 0.4 = 58 Amps

which is what id expect. any help would be appreciated.
 
And always come up with a totally unrealistic end figure!! lol!!!


Overcompensation it may be.

But I would rather go with the guidance and instruction of the nationally recognised productions in the court of law than guess work.
 
Overcompensation it may be.

But I would rather go with the guidance and instruction of the nationally recognised productions in the court of law than guess work.

Overcompensation, ....that has to be the understatement of the year!!

Come on Widdler, we both know that the criteria within BS 7671 and it's guide doesn't work and come to that has never worked!! I have never seen or known of a single Electrical Design Engineer/Consultant etc, ever use them either!!!

You may need to support and use them as a collage lecturer, ...but they are going to be of little use to anyone outside that collage classroom...
 
- - - Updated - - -

Overcompensation, ....that has to be the understatement of the year!!

Come on Widdler, we both know that the criteria within BS 7671 and it's guide doesn't work and come to that has never worked!! I have never seen or known of a single Electrical Design Engineer/Consultant etc, ever use them either!!!

You may need to support and use them as a collage lecturer, ...but they are going to be of little use to anyone outside that collage classroom...


I'M DONE WITH THIS.
 
the OSG and bs7671 only give very basic guidlines on diversity , mainly for domestic installs with very conservative figures.
move onto big commercials etc , then diversity takes on a much more important and complex role , otherwise we'd be using 25mm for lighting on the top floor of 6 storey office block ;-)

so at this point the designer has to go beyond suggested " one size fits all" tables and look more closely at assessing demand.
 
I would imagine it comes from 100 yrs of experience of supplying electrical supplies. Diversity is one area where there is no hard and fast formula, every, literally every, installation will have an amount of diversity applied and every one will and could be different.
 
Totally agree with Malcolm, the X0.4 is a good starting point when assessing diversity, but this must be applied in light of experience.
 

Similar threads

I
Replies
5
Views
18K
J

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
applying diversity
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
27
Unsolved
--

Advert

Thread statistics

Created
ianphilip007,
Last reply from
dagrat,
Replies
27
Views
9,307

Advert