I
ianphilip007
hi guys
ive got myself a little confused here when trying to calculate a max demand figure for the installation below.
60amp TNCS supply to a bungalow.
1x 30A Ring Main
1x 30A cooker unit(with socket)
1x 40A Shower (8.5kw)
2x 20A Radials
1x 5A Lights (7x100w)
using table 1B app 1 OSG
ring main (30a) no diversity = 30A
cooker unit(30a) 10A+30%(fl)+5A =24A
shower(40a) no diversity = 36.9A
radial(20a) 40% = 8A
lights 66% =3.04A
using these figures it comes out at a diversified current of 109.9Amps what am i forgeting as this cant be right can it? do i have to apply diversity to the diversified currents
when i use my usual method of adding up the MCB's and then multiplying by 0.4
40+30+30+20+20+5 x 0.4 = 58 Amps
which is what id expect. any help would be appreciated.
Ian the 0.4 is exactly the method I use and was shown to me by a DNO engineer many years ago as a good rule of thumb, and something I always use as that a rule of thumb, so IMO mate that looks just about right.
The thing is the shower. Quite right the OSG do have the take that it is a fixed load, and so no diversity, I always felt that was the right way to think when you look at it as a final circuit, but not in an installation as a whole.
As said before the OSG is a good guide, but it is just that, and even this tells us in the section on diversity that there are many ways to treat the subject, and eventually the amount of diversity done is purely down to the designer and experience.
thanks Malcom
i usually times the total of the breakers by 0.4 (rule of thumb) for max demand.
when using the OSG table 1B to work out diversified currents would this total figure then be multiplied by 0.4 ? if this is correct then it makes sense.
on a similar note ive noticed that the OSG states that "the C.U should be of a sufficent rating to take the total load connected to them with out the application of any diversity".
so in the case above the total load connected would be 125Amps if no diversity applied. i find this very confusing and hard to understand. help pls lol
With working out the maximum demand and applying diversity I get approx 74.2 Amps. (I have not referred to the book for it though).
What current rating is the unit?
its 60 amp main fuse, the rating of the mainswitch of the unit is 63Amps
Well I'd advise to either reduce the demand of the shower or increase the nature of the supply.
widdler how did you come up with the 74.2A ? is that by using the OSG table 1b and applying diversity or by adding mcb's ratings and x 0.4 ?
max demand.JPG just somthing in one of my books
I use the IET design guide.
hi guys
1x 30A Ring Main
2x 20A Radials
lights 66% =3.04A
In reality, you would be hard pushed to see even that 58Amps flowing in your bungalow!! Even if you did, it would only be for a few minutes at most. ...lol!!
I think the max demand calculation needs a rethink. It works fine if its a small house with six circuits, but goes to poo when its a large barn conversion with six socket circuits, six lighting circuits, in a twenty way board!
just a thought i have.
32x4 rings
16x1 radial combi boiler
40x1 cooker
6 x4 lights
total 208x0.4=83.2 amps
at the moment it has a 60 amp main fuse and working fine,will get dno to put larger one in though.
the chances of them using half the load would be something though
hi guys
1x 30A Ring Main
2x 20A Radials
lights 66% =3.04A
I think we missed something in the OP.
When you do by OSG, you not going by the fuse size, you going by the load size, so for cooker you apply all that 30% and everything to the load not fuse, unless it really draws 30A as you say, but that means your cooker is 6.9kW, is that correct.
And shower only draws 37A if to go by load, 8500/230=37A
But anyway, to do by OSG would be a big sum, I like everyone else, go by 40% rule.
Best regards: Al
I
18K
J
applying diversity
Australia
ianphilip007,
dagrat,