TT Supply.
Main CU, With earth to rod outside.
Second CU for storage heaters, Also on a seperate Rod outside.
I have been told this second rod is not needed for the second board, Aslong as the resistance of the first earth on the 1st CU is within the reg limits (lower than 200 Ohms) then the first rod can also earth the second CU. Is this correct?
Ive measured the first main Rod to be 123 Ohms, I know its unusually high but its within the limits..
What do you lot think?
1 rod is fine link ed to both boards and 123 ohms is afine for tt system 200 ohms is only a recomendation and higher resistances are still acceptable
regards tux
.... 123 ohms is afine for tt system 200 ohms is only a recomendation and higher resistances are still acceptable
regards tux
Indeed it is only a recommendation, however it is said that anything over 200ohms could be unstable.:)
All the above are correct.
All you need is an earth and a main earth terminal which both boards can use.
However , there is nothing wrong in using 2 rods linked to give you a lower earth reading.
Reply to Are 2 Earth Rods Needed ? in the Australia area at ElectriciansForums.net
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
I have just watched one of John Ward's interesting videos - It all makes sense apart from one of the final points involving adding an earth rod...
4K
Hi installing my first solar PV on my own home before starting the courses next year and need some advice on earthing PV. System 6kw solar PV - 2...
7K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...