Discuss Asked to bond a sink (table) in the UK Electrical Forum area at ElectriciansForums.net

The 23k "rule" is wiring regulations, not PME regulations. Bonding, which is reqd in this situation and creating an equipotential zone ensures the safety of the area. What does create danger is bonding bits of pipe etc and not others, as enviged by the wiring regulations. For example, bonding an oil pipe but not a water pipe "because its got an insulated insert" Regards UKPN, and mind how you go.

If our man tests these metal sinks in question on a hot day with nobody working and nice dry floors, no way will they need bonding.

I'd defer the problem to the summer.
 
Bonding a sink that isn't extraneous doesn't do anything to help the work done because it didn't affect the integrity of it or accessible from outside it. If the neutral was lost the whole zone would end up at the same level so that wouldn't be the additional hazard in most cases.
Bond/earth it or not you'd still need a double fault to receive a shock.
The additional hazard would actually be in the case of a double fault situation where live parts were accessible. Touching the bonded sink and the live part would cause a shock.
 
I’ve had this same problem, an insurance inspection in a commercial kitchen recommended the bonding of free standing stainless tables with plastic feet!
I said I was pretty sure it wouldn’t need bonding under the current regs but on testing them they came out as extraneous I can’t recall the exact reading but they were somewhere in the danger zone 1.6k to 22k.
It must have been the grease providing a path.
Anyway I rang my scheme and they told me to bond them all. The site neutral was 240mm I think so it would have meant installing a 50mm
conductor to each table!
I never did suss out s solution as they demo’d The whole building about a month later and built a brand new one!
 
John, I don’t understand the first half of your post. Cheers.
Sorry, i should be banned from posting after midnight as i literally didn't proof read it! See corrected version with edits on bold:

Bonding a sink that isn't extraneous doesn't do anything to help the equipotential zone because the sink didn't affect the integrity of it and isn't accessible from outside the zone. If the neutral was lost the whole zone would end up at the same level so that wouldn't be the additional hazard in most cases.
Bond/earth it or not you'd still need a double fault to receive a shock. The zone is there to prevent single fault conditions from being able to cause a shock.
The additional hazard would actually be in the case of a double fault situation where live parts were accessible. Touching the bonded sink and the live part would cause a shock.
 
they demo’d The whole building about a month later and built a brand new one!
That's one way around the problem!

If they are within the zone entirely it must have been the solid floor providing the path, although digging it up and installing mesh might have been even more impractical than bonding with 50mm flex
 

Reply to Asked to bond a sink (table) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So a quick catch up so you can get an idea… I was asked to do a job for another electrician, as he is too busy. I’m busy myself but said I’d...
Replies
18
Views
2K
Just want to know everyone’s approach to testing bonding within houses. I do a lot of EICRs, and I would say more times than not I can never get...
Replies
5
Views
1K
Good morning everyone. I’m looking at getting an EV charger installed at my home and the company is requesting that I earth bond my water supply...
Replies
8
Views
4K
Evening all, Recently started working for a company carrying out electrical installations - I've found a job today that didn't have any bonding...
Replies
8
Views
2K
Hi sorry very long one. Please hop to bottom paragraph for short version. I’m just about to refurb bathroom in my 1986 house but bonding always...
Replies
36
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock