I recently had a call out to look at a lighting circuit that had an Aurora Dimmable Transformer 50 - 210 W/VA feeding two seperate spotlight circuits. One has three spotlights which are working fine. The other has six with three working fine and three just about lit. The transformer is therefor incompatible. Any suggestions as too what transformer to replace the existing unit?
 
u have that one tranny supplying all 9 spots or is there one for each circuit? if it's just the one then is no wonder it's struggling.

if the existing one's still working it'll be fine on the 3 spots circuit. as for the other circuit, gonna have to split it up if possible, 2x3, 3x2; don't think you'll find a tranny capable of running the 6 spots.
 
Would it not be easier to just choc block it? Therefore no need for the transformer?
 

Reply to Aurora transformer in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock