richiep

hello, if all the zs values are within parameters , do you not need to install a 4mm earth in a bathroom? looking at doing a cu change at a property where bathroom is tiled from floor to ceiling! would it fail an assessment ? thanks
 
Before changing consumer units its best to be 100% sure of what is expected for you to comply with the latest Regs. Anyone who has sufficient training would not be asking this question.
 
I have never installed a 4mm in a bathroom, mind you domestic's not my thing.

Make sure the clamp does not squash the white pipes as they are not as strong as the old copper ones.
 
Have a look at 701.415.2 in the BGB....or the OSG explains.
If you dont have access to those two publications you should not be carrying out the work.
 