My understanding of it is that to comply with the 17th it needs to be protected by RCD.
also there is only a need for an "isolation switch" if there is no window in the room it is being fitted.
hope this helps.
that is ridiculous! windows?????!! get a grip man.
Yeah thats it.
I've asked this question elsewhere on the web and there seems to be so many different answers. Some say yes you definetly have to and others say only if it has no window and some say it needs a switched fused spur - it also says this in the instructions.???????????
HELP....i dont know which answer is right.. It would be better if i need no isolator at all then i can just go ahead as i wanted.
if someone can shed some light on this with some form of regulation or something it would be great.
also the lights are also wired in twin and earth shall i put a small junction box on and wire the fan and the transformer in flex?
whoever is talking about windows and wiring regulations in the same sentence IS OFF THERE HEAD.
its this simple my friend....
1. if its a timer fan ( mounted in loft ) it needs a 3 pole isolator located outside zones 1 and 2 or in the loft / outside etc
2. if its a timer fan with light you need the 3 pole isolator AND 30mA RCD protection ( bath regs )
3. if its a timer fan in the wall you need 3 pole isolator and RCD
4. if its a fan in the wall that only comes on with the light and has no perm supply then you only need RCD protection.