Recently went to a house where there is a separate supply and FSU for a boiler that is situated in the bathroom. It is 2.5 mm cable and has the correct breaker at 16A. The FSUs are outside the zones.
Another FSU is wired to this one to supply a pull cord for the extractor fan. Presumably because it was too difficult to get the supply from the light circuit.
The boiler service engineer told the owner he didnt like this arrangement. He also commented on his service notes. The owner doesnt know what the reason is and the sentence about it on the report is unreadable.

Is there anything wrong with this arrangement if everything is correctly fused ?
 
Must be one hell of a boiler requiring all 16A of that circuit.

I suspect the unintelligable comment by the plumber - sorry heating consultant speaks volumes.
 
As long as its obvious what each isolator is for i cant see a problem. Assuming the spur has the correct fuse if course
 
it may be a spur off a spur but i understand it is a radial so it will not be a problem
 
If all requirements are met regarding fusing, zoning, rcd's and load I think its fine.......you see it many times in a kitchen from the ring main with boiler, fan, sockets etc
 
The boiler service engineer told the owner he didnt like this arrangement. He also commented on his service notes.

He sounds like someone who knows a tiny weeny bit and nothing else, the most dangerous people are those who know a bit, they think they know everything and get nearly everything wrong, he's also a plumber I suspect and therefore completely brain dead :90: :41:
 