New bathroom as an extension. Normally if theres going to be a wall mounted extractor fan I take the 2 core from the switch and loop in and out of the lights. From the same switch I take a 3 core to above outside the door for a fan isolator then a 3 core from the isolator to the wall fan.
In this case the owner wants to put a fan in the ceiling that has an integral light in it, it looks a bit like a downlight. Do I wire it like the above case or just loop in and out and treat it like a light ?
Thanks for any help.
 
like malcome has said manufacturers instruction , most now require a 3 amp fuse to protect the fan ,so i would take the loop in and out to a fused spur then a feed to the light from there run a three core to a fan isolator and then to the fan , this way does protect the bathroom lights as well but you have to protect the fan not only the live but the switched live to
 
and don't forget RCD protection for all circuits in the bathroom is essential.
 