going to first fix bathroom refit tommorrow, everything ok RCD, bonding etc but fan is to be located over bath at height of 2.4mts (high ceilings). this seems ok with zones in regs but is it good practice or should I fit low voltage
 
as long as it's fit for the environment. i would insist on IP44. 230V is OK as it's outside zones.
 
I would just check the manufacturers instructions as i nearly bought a 230V fan based on its IP rating and then (in the wholesalers) i opened up the box and had a read.
"quote" - "These fans must not be installed above a bath or shower"

They were primeline fans, ended up with 12V jobbies.....
 
or use an in line fan mounted in the loft.
 
Aah, the old 'this fan is splash proof as long as it doesn't get wet' clause - as you say, worth checking the instructions.


I would just check the manufacturers instructions as i nearly bought a 230V fan based on its IP rating and then (in the wholesalers) i opened up the box and had a read.
"quote" - "These fans must not be installed above a bath or shower"

They were primeline fans, ended up with 12V jobbies.....
 
Aah, the old 'this fan is splash proof as long as it doesn't get wet' clause - as you say, worth checking the instructions.

I dont do much domestic so when asked to replace 2 fans in a bathroom, thought i would get the book out , checked zones and IP rating and then went off to wholesalers. 12V fans were already ftted but broken and i did think it was overkill and a couple of 230V fans would be a cheapish fix. Dont know why i got the box open, maybe bored waiting for the invoice but i did think friggin cop out, along with DP switch and 3A fuse, think basically they are taking no risks.
 