Jon Hodgson

I'm adding a new Shower and Shower CU to a property that has no equipotential bonding to it, main bonds are in place though. Existing CU no longer in production and nothing to retro fit into it.

The question is do I NEED to change the light in the bathroom to IP rated as its inside zone 2 and since I will be having to work on the lighting circuit when i do the bonding. I have already recommended it to the customer but haven't said that it needs to be done as yet and just thought I'd clarify.

Most of the time this suggestion is taken and they change it but this time the budget is a bit more of an issue.

Thanks

Jon
 
Remember zone 2 is up to 1.25m above the floor, it's surprising how many bathrooms are higher than this. In which case it would be outside the zones.
 
Most houses I've lived in have 8 or 10 foot ceilings. The 2.25 (7' 4 1/2") limit means lighting is not an issue. Perhaps its where I live. Can see it being an issue in Cornwall cottages
 