Discuss Bathroom UFH earth mesh in the Electric Underfloor Heating Wiring area at ElectriciansForums.net

marcuswareham

Esteemed
Arms
Reaction score
199
Whist looking up something unrelated in section 701, I noticed reg 701.753

Stating that underfloor heating wire in a bathroom must have an earthed sheath or metallic earth grid etc etc & that electrical separation shall not be used

It got me thinking, the underfloor heating wire I used in my conservatory has no earth and is double insulated (different version in the bathroom).

Although I don't have an issue I am wondering if someone was to find underfloor heating in a house whilst doing a repair or an EICR or whatever and It was in a bathroom / shower room , and there was no earth conductor present or evidence to suggest it has an earth mesh, sheath or enclosure. What would you do as I can imagine if you tell the client you need to remove the bathroom floor I doubt that would go down well, and as the reg states using an isolation transformer is also not allowed?
 
EICR or whatever and It was in a bathroom / shower room , and there was no earth conductor present or evidence to suggest it has an earth mesh, sheath or enclosure. What would you do


Hi, I’m a simple person and so if I’m doing a Report, I report what I find :) .
 
Double insulation isn't normally considered as a means of protection in a dwelling so this is an interesting question. Why don't you email the manufacturer.
 
I'm not sure how you would go about ascertaining whether a mesh has been installed or not. You can only inspect what you can see.
 
If there was no earth on the ufh cable and no mesh and it’s within Zone 2 then the only fix I can think of would be to decommission it, sorry. Hopefully someone has another thought …
 
If there was no earth on the ufh cable and no mesh and it’s within Zone 2 then the only fix I can think of would be to decommission it, sorry. Hopefully someone has another thought …

Dont be sorry, I dont have this problem my bathroom UFH has earth

was just question i wall mulling over and trying to work out if there could be any other solution, as you say probably not
 
Double insulation isn't normally considered as a means of protection in a dwelling so this is an interesting question. Why don't you email the manufacturer.
I find that "double insulated" accessories are becoming increasingly problematic from a testing(EICR) point of view. It's sometimes difficult to know if you have discovered an unearthed appliance or simply found a "double insulated" appliance. "Double insulated" appliances can look just as "metallic" as their class 1 cousins. Just today I brought home a metallic "double insulated" downlighter removed from an install to add to my growing collection of "baffling" "double insulated" accessories.
 
Does zone 2 extend to beneath the floor?
Hi - no, but my interpretation of Reg 701.32.1 (last paragraph) is the heating mat being part of the floor means the zone requirements apply. Just my opinion and I am extending beyond what is written, as the reg only states this for walls and ceilings.
If we weren’t in a bathroom then 753.411.3.2 says Class 2 mats may not require the extra metal grid / mesh.
 

Reply to Bathroom UFH earth mesh in the Electric Underfloor Heating Wiring area at ElectriciansForums.net

Similar Threads

I am installing a Victron Quattro in an island mode configuration (in the UK, the DNO is the NG). I will be adding a stand-by generator. My...
Replies
3
Views
1K
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
195
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi guys, I'm trying to find a definitive answer on the use of 1.5mm 2C+E for power points in a transportable structure which is fed by a 15A inlet...
Replies
2
Views
2K
Hi all, Been a while since I've posted - got a new project to install a small 7kw electric shower. The shower will be about 7 metres from the...
Replies
84
Views
11K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock