Discuss Bathroom UFH earth mesh in the Electric Underfloor Heating Wiring area at ElectriciansForums.net
marcuswareham
Whist looking up something unrelated in section 701, I noticed reg 701.753
Stating that underfloor heating wire in a bathroom must have an earthed sheath or metallic earth grid etc etc & that electrical separation shall not be used
It got me thinking, the underfloor heating wire I used in my conservatory has no earth and is double insulated (different version in the bathroom).
Although I don't have an issue I am wondering if someone was to find underfloor heating in a house whilst doing a repair or an EICR or whatever and It was in a bathroom / shower room , and there was no earth conductor present or evidence to suggest it has an earth mesh, sheath or enclosure. What would you do as I can imagine if you tell the client you need to remove the bathroom floor I doubt that would go down well, and as the reg states using an isolation transformer is also not allowed?
Hi, I’m a simple person and so if I’m doing a Report, I report what I find :) .
Double insulation isn't normally considered as a means of protection in a dwelling so this is an interesting question. Why don't you email the manufacturer.
I'm not sure how you would go about ascertaining whether a mesh has been installed or not. You can only inspect what you can see.
If there was no earth on the ufh cable and no mesh and it’s within Zone 2 then the only fix I can think of would be to decommission it, sorry. Hopefully someone has another thought …
Dont be sorry, I dont have this problem my bathroom UFH has earth
was just question i wall mulling over and trying to work out if there could be any other solution, as you say probably not
I find that "double insulated" accessories are becoming increasingly problematic from a testing(EICR) point of view. It's sometimes difficult to know if you have discovered an unearthed appliance or simply found a "double insulated" appliance. "Double insulated" appliances can look just as "metallic" as their class 1 cousins. Just today I brought home a metallic "double insulated" downlighter removed from an install to add to my growing collection of "baffling" "double insulated" accessories.
Does zone 2 extend to beneath the floor?
Hi - no, but my interpretation of Reg 701.32.1 (last paragraph) is the heating mat being part of the floor means the zone requirements apply. Just my opinion and I am extending beyond what is written, as the reg only states this for walls and ceilings.
If we weren’t in a bathroom then 753.411.3.2 says Class 2 mats may not require the extra metal grid / mesh.
Reply to Bathroom UFH earth mesh in the Electric Underfloor Heating Wiring area at ElectriciansForums.net
I am installing a Victron Quattro in an island mode configuration (in the UK, the DNO is the NG). I will be adding a stand-by generator. My...
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Hi guys, I'm trying to find a definitive answer on the use of 1.5mm 2C+E for power points in a transportable structure which is fed by a 15A inlet...
Hi all, Been a while since I've posted - got a new project to install a small 7kw electric shower. The shower will be about 7 metres from the...
11K
