Reselling and making a profit ??Be interesting to know how the electric is being charged if tenants have card meters and it all runs through the Landlords meters.
Reselling and making a profit ??
Each flat will have its own consumer unit covering 3/4 circuits, there not large flats, more like studio flats, there will be a means of isolation in each flat via the flats cu , just wondering the best method of providing isolation at the main board, does there need to be individual isolation there to as it is now, each flat will be on its own MCB at the main board. Also at the landlords main board there will be the F/A and two landlords circuits for communal hallways. The card meters in the flats are sub meters, the landlord sells the cards to the tenants .All of the flats could be fed from a single DB, however it should not be an MCB distribution board. For any hope of discrimination each flat needs to be fed via a fuse or possibly an MCCB.
With that in mind it will almost certainly be cheaper to install a switched fuse for each flat supply.
Then there is also the future convenience of operation to be considered, it will be far better to have seperate switchgear for each flat to allow any future work to be done without disturbing other flats.
The size of the supply for each flat needs to be calculated and the cable size calculated.
If you have been a trainee but aren't now then that implies you are now, and fairly recently, fully qualified so you should have the knowledge to carry out cable calculations far better than just guessing at 6/10 maybe.
Each flat will have its own consumer unit covering 3/4 circuits, there not large flats, more like studio flats, there will be a means of isolation in each flat via the flats cu , just wondering the best method of providing isolation at the main board, does there need to be individual isolation there to as it is now, each flat will be on its own MCB at the main board. Also at the landlords main board there will be the F/A and two landlords circuits for communal hallways. The card meters in the flats are sub meters, the landlord sells the cards to the tenants .
yea im a professional, but not taken on this type of job before, the landlord is trying to save money, i think hes realised that hes going to have to get this work done, i also need the work at the moment so its difficult to turn down, i trying to go along with what he wantsDo your diversity/load calculations on the whole block, is it more than 100A?
What is the main fuse?
Have you measured supply impedance (for PSSC) and ground fault impedance (Zs for PFC)?
If the landlord is a tight-wad and not going to do it properly, and it is below the 100A limit, so a MCB board is the only option then at least get something like a 12-way or 14-way so you can put blanks between each of the flat's MCBs (and final landlord's circuit) to reduce mistakes in switching two at once, etc. Also get one with a 300mA type-S RCD incommer to protect the feed cables, and put all flats on RCBO (or worst case a local 30ma RCD) for safety on their own boards. Also landlord's circuits on RCBO as well.
Probably worth putting in an SPD there as well, that takes 2 of the ways up.
If you want any sort of reasonable discrimination with a MCB you will need the upstream one (i.e. per flat in the main board) to be something like a 50A D-curve and/or to set the flat's own rings on a 20A B-curve breaker instead of the "normal" 32A.
From that upstream MCB you get another constraint on cable size based on final (flat consumer unit) unit Zs for adequate fault clearance time, above the rating for 50A thermal (or whatever). Hence your measured supply Zs from the earlier comment!
Check the regs, crunch the numbers, and don't believe me as I'm just a passing stranger...
[automerge]1584620505[/automerge]
Actually the flat feeds would be "distribution circuits" I guess so a 5 sec disconnect time is OK, that would ease the max Zs value for a 50A D-curve to somewhere around 0.4 ohm.
Again, check that and compute max length for your cable of choice and its supply and earth impedance per meter values. You are the professional who is doing it!
yea i am a professional but ive not taken on this type of job before, the landlord is trying to save money, im trying to go along with what he wants but i have to make sure its all inline with the regs.Do your diversity/load calculations on the whole block, is it more than 100A?
What is the main fuse?
Have you measured supply impedance (for PSSC) and ground fault impedance (Zs for PFC)?
If the landlord is a tight-wad and not going to do it properly, and it is below the 100A limit, so a MCB board is the only option then at least get something like a 12-way or 14-way so you can put blanks between each of the flat's MCBs (and final landlord's circuit) to reduce mistakes in switching two at once, etc. Also get one with a 300mA type-S RCD incommer to protect the feed cables, and put all flats on RCBO (or worst case a local 30ma RCD) for safety on their own boards. Also landlord's circuits on RCBO as well.
Probably worth putting in an SPD there as well, that takes 2 of the ways up.
If you want any sort of reasonable discrimination with a MCB you will need the upstream one (i.e. per flat in the main board) to be something like a 50A D-curve and/or to set the flat's own rings on a 20A B-curve breaker instead of the "normal" 32A.
From that upstream MCB you get another constraint on cable size based on final (flat consumer unit) unit Zs for adequate fault clearance time, above the rating for 50A thermal (or whatever). Hence your measured supply Zs from the earlier comment!
Check the regs, crunch the numbers, and don't believe me as I'm just a passing stranger...
[automerge]1584620505[/automerge]
Actually the flat feeds would be "distribution circuits" I guess so a 5 sec disconnect time is OK, that would ease the max Zs value for a 50A D-curve to somewhere around 0.4 ohm.
Again, check that and compute max length for your cable of choice and its supply and earth impedance per meter values. You are the professional who is doing it!
does there need to be individual isolation there to as it is now, each flat will be on its own MCB at the main board.
im not ignoring the advice , clearly protecting each sub main with an MCB is not the way to go about it.So you'll be ignoring the above advice, and the regulations, regarding discrimination and protecting each submain with an MCB?
[automerge]1584624357[/automerge]
From the picture it looks like the label says there's and 80A fuse in the cutout.
I'd want to carry out a load study first off to assess the actual demand on the supply to see if there is not a bigger problem.
So you'll be ignoring the above advice, and the regulations, regarding discrimination and protecting each submain with an MCB?
From the picture it looks like the label says there's and 80A fuse in the cutout.
I'd want to carry out a load study first off to assess the actual demand on the supply to see if there is not a bigger problem.