Do your diversity/load calculations on the whole block, is it more than 100A?
What is the main fuse?
Have you measured supply impedance (for PSSC) and ground fault impedance (Zs for PFC)?
If the landlord is a tight-wad and not going to do it properly, and it is below the 100A limit, so a MCB board is the only option then at least get something like a 12-way or 14-way so you can put blanks between each of the flat's MCBs (and final landlord's circuit) to reduce mistakes in switching two at once, etc. Also get one with a 300mA type-S RCD incommer to protect the feed cables, and put all flats on RCBO (or worst case a local 30ma RCD) for safety on their own boards. Also landlord's circuits on RCBO as well.
Probably worth putting in an SPD there as well, that takes 2 of the ways up.
If you want any sort of reasonable discrimination with a MCB you will need the upstream one (i.e. per flat in the main board) to be something like a 50A D-curve and/or to set the flat's own rings on a 20A B-curve breaker instead of the "normal" 32A.
From that upstream MCB you get another constraint on cable size based on final (flat consumer unit) unit Zs for adequate fault clearance time, above the rating for 50A thermal (or whatever). Hence your measured supply Zs from the earlier comment!
Check the regs, crunch the numbers, and don't believe me as I'm just a passing stranger...
[automerge]1584620505[/automerge]
Actually the flat feeds would be "distribution circuits" I guess so a 5 sec disconnect time is OK, that would ease the max Zs value for a 50A D-curve to somewhere around 0.4 ohm.
Again, check that and compute max length for your cable of choice and its supply and earth impedance per meter values. You are the professional who is doing it!