Hi all

Called to do an EICR on a property 4 studio flats / bedsits within a single house.
The t&e sub main to each flat runs within the fabric of the building and has a 30mA RCD at its distribution point...assuming this was an add on to the original installation.

Each flat has a RCD main switch consumer unit also with a 30mA .. hence no discrimination between the 2.

The consumer units for each flat are by the flat front door and the communal halls are lit by the landlords supply and emergency lighting.

What would you code for no discrimination between RCD's ..? .. my feeling is its c3 at the most as i cant see its causing any danger .. the distribution RCD's are on the ground floor and are accessible to be reset if required .. if the flat occupier can get to the flat consumer unit to reset that RCD they can exit the flat door into a lit corridor to reset the distribution RCD ..

All thoughts gratefully accepted

cheers

Vito
 
That means they can also turn off a neighbour that they don’t get along with.


The distribution T&E only requires rcd protection if buried less than 50mm. If it’s deeper than that, or clipped surface, or in trunking where it’s visible, then it doesn’t need rcd.
 
That means they can also turn off a neighbour that they don’t get along with.


The distribution T&E only requires rcd protection if buried less than 50mm. If it’s deeper than that, or clipped surface, or in trunking where it’s visible, then it doesn’t need rcd.
They would be able to switch off a neighbor with a main switch or mcb ! .. so thats not an issue.

Sub mains are looking chased in .. so likely less than 50mm deep .

I was looking for advice on a eicr code.!
 

Reply to EICR code for lack of discrimination between RCD's in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
802
Did a couple of inspections on 2 x 2 bed ground floor flood damaged flats today, only 4 circuits in each, bizarrely one socket circuit and 2...
Replies
6
Views
2K
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
What are peoples opinion's on this, pair of big old semi-detached houses (85 and 87) converted into apartments, dont think its a HMO although it...
Replies
1
Views
244
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock