Re flats: Generally now all meters to each flat have to be on the ground floor altogether in a community room whereby each tenant/ owner has 24 hour access. The DNO would have to install a suitable sized mains cable (possibly 95cne) into a Ryefield box to cater for 11 flats plus "Landlords supply" for corridor lighting and fire alarm. From the Ryfield box a separate cable to a 60/80amp cut out (header) fuse is supplied for each flat. The supplier will the connect a separate meter to each and every flat. A suitable sized switch fuse is then fitted by the electrician, running a separate sub main to each flat consumer unit. To accommodate all the DNO's equipment , meters, switch fuses etc a large area is required. Basically all the cut -out fuses and meters are next to each other along with the switch fuses.