just been to quote a CU change. old wylex rewireable. as soon as in was in the door, customer tells me new bonding installed to boiler. OK. takeas a quick look. new boiler, 10mm bonding cable from TNC-S terminal to gas pipe at boiler, ( this connection is approx. 600mm from where the gas pipe enters the property from external gas meter) so far , so good. from this bond, all pipes at boiler are cross bonded, n o doubt done by the boiler fitters. next , back to CU, main earthing cable to CU is either 4mm or 6mm, so needs to be upgradeed to 16mm, no problem. next visit to water service. original 4/6mm cable has been disconnected from pipework when a water meter was installed. now, here's the silly bit. water enters in plastic pipe with a metal stop tap. then some fancy plumbing that wouldn't put an oil refinery to shame, water meter and then a 10mm bonding conductor from the stop tap tp the consumer side of the water meter. now, the water pipes are isolated from true earth at this point., but bonded to the gas at the boiler. my thoughts are to disconnect the bond at the water meter, IR the pipework to the MET to determine whether extraneous or not. thoughts, please.