When rewiring a dwelling and installing a 17th ed board what bonding is required, main bonding, gas and water, supplementary? thanks
Last edited by a moderator:
Sure it's been asked many times, plastic supply pipe, stop cock under the floor, around a metre of copper then multiple plastic fittings etc etc. I'm not gonna install Main Bond to the water service, anyone think I should? Clearly I've done the gas.
Sorry should say if it's tns or tncs 16mm main bond 10mm to gas and water if it's tt only 6 mm to electrode