When rewiring a dwelling and installing a 17th ed board what bonding is required, main bonding, gas and water, supplementary? thanks
 
Last edited by a moderator:
If its a electrodess 16mm main bonding 10mm to water and gas if it's tt only 6mm required to electrode
 
Sorry should say if it's tns or tncs 16mm main bond 10mm to gas and water if it's tt only 6 mm to electrode
 
Sure it's been asked many times, plastic supply pipe, stop cock under the floor, around a metre of copper then multiple plastic fittings etc etc. I'm not gonna install Main Bond to the water service, anyone think I should? Clearly I've done the gas.
 
Sure it's been asked many times, plastic supply pipe, stop cock under the floor, around a metre of copper then multiple plastic fittings etc etc. I'm not gonna install Main Bond to the water service, anyone think I should? Clearly I've done the gas.

No point, no potential is being introduced into the property.

Sent from my GT-I9100 using Tapatalk
 
im sure i read somewhere that if you bond a plastic pipe it actully increases the risk
 
Sorry should say if it's tns or tncs 16mm main bond 10mm to gas and water if it's tt only 6 mm to electrode

Really? So all installations just require the same do they regardless of any other influences?
 