Hi all,

Just a quick question.

When bonding tray or basket, is it acceptable to take an earth from the nearby trunking, using 4/6mm with a crimp lug?

Saves running back to DB :)

Thanks
 
well as part of the electrical installation...it`l be earthed....wont it...
seems some still cant grasp what is earthed....and whats bonded....and the roles each play....
 
well as part of the electrical installation...it`l be earthed....wont it...
seems some still cant grasp what is earthed....and whats bonded....and the roles each play....

there's quite a good book out on the subject that explains both thoroughly and concisely. It's by a Mr Cockburn I believe.
 
question being... is the tray an exposed conductive part of the installation? if so then you earth it. if it's extraneous, then you bond it. IMO, it's part of your installation and should be earthed. tin hat firmly on.
 
question being... is the tray an exposed conductive part of the installation? if so then you earth it. if it's extraneous, then you bond it. IMO, it's part of your installation and should be earthed. tin hat firmly on.

I agree...................
And.............if it can't become live due to basic insulation failure and it's not extraneous then you leave it alone:)

I think..............................:dunce:
 
if it's carrying SWA then it can't become live, not sure about T/E though. seen some T/E ragged on installation. i'd earth it then.
 
Best bet would be to ask your site foreman/clerk of works and ask what he wants to see. It's bound to be different from what's actually required. :wink_smile:
 
Tel`s right...any cable thats screened/armoured is unlikely to go to fault though anything other than other cores or the armourings....
its stuff like flat twin where you would be thinking about it......
as its only single insulated....
 
Hi all,

Just a quick question.

When bonding tray or basket, is it acceptable to take an earth from the nearby trunking, using 4/6mm with a crimp lug?

Saves running back to DB :)

Thanks

So why not earth the tray-work from the DB where it is supposed to be earthed from?? Don't forget, any change in levels to the tray system, will also need to be linked across....
 
if it's carrying SWA then it can't become live, not sure about T/E though. seen some T/E ragged on installation. i'd earth it then.

Well if you think I'm going around and taking 'several thousand' of my earths and bonds off my traywork with SWA on them you can think again bonny lad............their staying put :omg_smile:
 
Well if you think I'm going around and taking 'several thousand' of my earths and bonds off my traywork with SWA on them you can think again bonny lad............their staying put :omg_smile:

Nah, get 'em off and weighed in! :-)
 