I take it no one here has GN8.
Exposed-conductive-parts of cables, such as the copper sheath of MI cable (or light fitting) are required to be connected to the MET of the installation by a CPC designed to conduct earth fault currents. The cable tray/basket to which the MI cable is attached, or may be in contact with, is not itself an exposed-conductive-part and therefore it does not require earthing. To do so would only serve to distribute further any touch voltages resulting from an earth fault on an item of equipment to which the cable is connected.
A cable complying with the appropriate standard having a non-metallic sheath or a non-metallic enclosure is deemed to provide satisfactory basic protection and fault protection, as does an item of class2 equipment. Class2 equipment is constructed such that any insulation fault in the cable cannot result in a fault current flowing into any conductive parts with which the equipment may be in contact. Hence the metal cable tray/basket need not be earthed.