Nah, get 'em off and weighed in! :-)

Lol.................I would but I earth (and bond) all my tray Swa or not.
Lots of hand-fisted fitters here with cranes swinging stuff all over the place..............not to mention the odd Class 1 light fitting dotted around the place and bolted onto the structure:).
 
Are you sure you need to earth or bond the tray/basket?
Have a little read of page 157 GN8 :wink_smile:

Depends what you and they mean by 'need to' really.

Do I think that it is possible in my installation for this tray to become live under fault conditions..........Yes.
That's why it's earthed:)
 
How will your tray become live under fault conditions if it is not earthed/bonded?
 
Last edited by a moderator:
How will your tray become live under fault conditions if it is not earthed/bonded?

Read my original post...............

Damage to cables caused by equipment hitting it with the overhead cranes.............not probable but could and nearly has happened.

Contractors coming on site and running T&E on the tray!!!.
Class 1 equipment bolted to it..........and yes I know this has it's own cpc but the tray would still become live until the fault had cleared.

I'm interested in your thoughts here.
 
Ok Im not saying tray/basket should not be earthed or bonded, but in most cases it is not required.
Allan have you got GN8 as both of your questions are answered on page 157
 
quote_icon.png
Originally Posted by Simlec
How will your tray become live under fault conditions if it is not earthed/bonded?

Are you actually being serious here?? Think about what you have written!! It won't become live if it ''IS'' earthed, hopefully the OCPD will clear any fault to earth. However if the tray/basket isn't earthed, then the metal containment can become live (as you put it) and stay that way until some poor bugger comes along and completes the faulted circuit....
 
Ok Im not saying tray/basket should not be earthed or bonded, but in most cases it is not required.
Allan have you got GN8 as both of your questions are answered on page 157

I have it and I've read it mate I just don't agree with it:)

edit.............as post above lol.
 
I take it no one here has GN8.

Exposed-conductive-parts of cables, such as the copper sheath of MI cable (or light fitting) are required to be connected to the MET of the installation by a CPC designed to conduct earth fault currents. The cable tray/basket to which the MI cable is attached, or may be in contact with, is not itself an exposed-conductive-part and therefore it does not require earthing. To do so would only serve to distribute further any touch voltages resulting from an earth fault on an item of equipment to which the cable is connected.

A cable complying with the appropriate standard having a non-metallic sheath or a non-metallic enclosure is deemed to provide satisfactory basic protection and fault protection, as does an item of class2 equipment. Class2 equipment is constructed such that any insulation fault in the cable cannot result in a fault current flowing into any conductive parts with which the equipment may be in contact. Hence the metal cable tray/basket need not be earthed.
 
Are you actually being serious here?? Think about what you have written!! It won't become live if it ''IS'' earthed, hopefully the OCPD will clear any fault to earth. However if the tray/basket isn't earthed, then the metal containment can become live (as you put it) and stay that way until some poor bugger comes along and completes the faulted circuit....

So could you give me an example of how it will become live and stay live. And not eg with T+E on tray!
 
I take it no one here has GN8.

Exposed-conductive-parts of cables, such as the copper sheath of MI cable (or light fitting) are required to be connected to the MET of the installation by a CPC designed to conduct earth fault currents. The cable tray/basket to which the MI cable is attached, or may be in contact with, is not itself an exposed-conductive-part and therefore it does not require earthing. To do so would only serve to distribute further any touch voltages resulting from an earth fault on an item of equipment to which the cable is connected.

A cable complying with the appropriate standard having a non-metallic sheath or a non-metallic enclosure is deemed to provide satisfactory basic protection and fault protection, as does an item of class2 equipment. Class2 equipment is constructed such that any insulation fault in the cable cannot result in a fault current flowing into any conductive parts with which the equipment may be in contact. Hence the metal cable tray/basket need not be earthed.

So do we now just earth the motors on appliances and machines but there's no need to earth the frames etc?

Also................99.99999999% of tray and containment will at some point be connected to an 'earthy' point somewhere.
A fault on any piece of equipment will/could raise 'ALL' metalwork to mains voltage.........this includes the tray IMO and for that reason I earth it............then bond it :)
 
I take it no one here has GN8.

Exposed-conductive-parts of cables, such as the copper sheath of MI cable (or light fitting) are required to be connected to the MET of the installation by a CPC designed to conduct earth fault currents. The cable tray/basket to which the MI cable is attached, or may be in contact with, is not itself an exposed-conductive-part and therefore it does not require earthing. To do so would only serve to distribute further any touch voltages resulting from an earth fault on an item of equipment to which the cable is connected.

A cable complying with the appropriate standard having a non-metallic sheath or a non-metallic enclosure is deemed to provide satisfactory basic protection and fault protection, as does an item of class2 equipment. Class2 equipment is constructed such that any insulation fault in the cable cannot result in a fault current flowing into any conductive parts with which the equipment may be in contact. Hence the metal cable tray/basket need not be earthed.


Believe what you will,...i will!! Cable tray/basket will be, and has been earthed on every project i've ever worked on, going all the way back to my training days!! How long will it be, before they say that metal trunking and conduit doesn't need to be earthed??

Words on a bit of published paper mean little to nothing to me, or anyone else, that have seen the results of faults involving unprotected exposed conductive metalwork and containment systems.
 
Ok lads put your guns away i'm not saying your right or wrong!
The tray/basket is not at fault here its how its used.

Eng I love the way you bond all tray/basket but when someone says there going to run a cpc in metal conduit on here you jump on them like a pack of wolves.(if my memory serves me correct)

"SWA, MI run on tray" earth or bond whats the point.
"Tray work connected to earth and then enters the building" bond within 600mm on entering.
IMO "T+E on tray" earth and treat as cpc like metal trunking/conduit
 
GN8 aims its guidance towards the fact tray is carrying insulated and sheathed cables, therefore in an ideal installation are probably not going to ever make the tray live, but surely as trunking and conduit carries insulated cables without sheathing, then not earthing these would be plain stupid.

Each one to their own and every job has its own merits
 