A

atkins_1

Do I need to bond the incoming water and gas to my garage conversion ? They are fed by plastic supply pipes. But then all copper through the 40 square foot building containing small bathroom. Utility room and office. The electric feed is 16mm 3 core armoured to an mk rcd 5 way board.
 
IR test from MET tyo exposed copper piework. if the reading is > 23kohms, don't bond.
 
Where from and to ? The earth bar in the board to anywhere local that is metal part of the water or gas ?
Is that a rule of thumb or a reg. ?
So why do we bond in the property then ?
Surly if a strip light came away from its fixing and fell onto the gas pipe running through the room and a live contact was made then the whole lot would become live includig the boiler ?
Bonding would trip the rcd.
Thoughts ???
 
From the MET, which will either be in the main CU or nearby to it, to the metal pipework you mentioned. Are you a spark?
 
Yeah , stil got q 's to ask tho.
Why from the met in the house to the pipe thats 20 metres away inside the garage seperated by plastic pipe.?

- - - Updated - - -

Yeah , stil got q 's to ask tho.
Why from the met in the house to the pipe thats 20 metres away inside the garage seperated by plastic pipe.?

- - - Updated - - -

Yeah , stil got q 's to ask tho.
Why from the met in the house to the pipe thats 20 metres away inside the garage seperated by plastic pipe.?
 
you bond pipework if it's liable to introduce an earth potential. not because it's there.
 
bonding in garage conversion

Do I need to bond the incoming water and gas to my garage conversion ? They are fed by plastic supply pipes. But then all copper through the 40 square foot building containing small bathroom. Utility room and office as well as the main workshop front containing 10 doubke sockets and varoius lights.
 
Where from and to ? The earth bar in the board to anywhere local that is metal part of the water or gas ?
Is that a rule of thumb or a reg. ?
So why do we bond in the property then ?
Surly if a strip light came away from its fixing and fell onto the gas pipe running through the room and a live contact was made then the whole lot would become live includig the boiler ?
Bonding would trip the rcd.
Thoughts ???

The strip light should have its casing earthed via the cpc of the cable supplying it (if class 1) or be double insulated. The boiler casing and adjacent pipework will, similarly, be earthed via the cpc of the boiler supply. It's hard to think of a situation with a properly installed and tested electrical installation to current regs whereby a length of pipework can remain live. (Not saying it can't happen.)
 
Re: bonding in garage conversion

No but you'll be needing RCD's and if theres a new circuit(s) involved, a registered competent sparky!
 