Hi every one, i have been asked to complete some one elses install, ( i know not a good situation ) and there is an issue with the bore water pump, when the pump operates the led wall lights on the staircase flicker very badly and this continues till the pump cuts out. The pump is a DAB activedriver M/M1 rated at 10 A max fed off a secondary dis board which also feeds the lights. Also on the staircase are led step lights but these are not affected by the pump. Any suggestions please to resolve ?. The dis board is fed with a 10mm T&E from the main Dis board off a 32 A mcb, seems a low rating to me.
 
If the 32A MCB isn't tripping I'd leave it alone. I'd be checking the volt drop on the dis board and it's circuits whilst the pump is running. Maybe also a loose termination somewhere or possibly high neutral-earth voltage if the LED's are on electronic drivers.

What testing did you do so far and what were the results?
 
Perform an IR and continuity check on the motor n cable just to confirm alls ok. Compare running current against pump rating. If higher, impeller or bearings could be tight/siezed.
 
Here we go again!

How can anyone help without information?
Many people will try to guess and probably lead you on a wild goose chase.

Get the test results.

I just don't get it. It's as if the idea of doing some basic tests that take seconds is comparable to climbing Everest.

It's not even as if you need an expensive specialist meter to detect if you've got volt drop under load, a flippin' £15 Maplin AMM will do the job quite happily.
 
I alway's like the old excuse, that normally comes out ...I didn't have my test equipement with meat the time!! Well why did you go to the job in the first place then... No matter how good an electrician you are, you're next too bloody useless without you're test equipement, that should Always be with you!!
 