Hmm, good point. In which case we could do with some more work, so go ahead and borrow this neutral, then when it doesn't work pay a sparky to come and sort it out. :)
 
Hmm, good point. In which case we could do with some more work, so go ahead and borrow this neutral, then when it doesn't work pay a sparky to come and sort it out. :)
why would it not work?
a typical reason please stroppy..
and code for a shared neutral on an ECR please...
 
why would it not work?
a typical reason please stroppy..
and code for a shared neutral on an ECR please...

I see what mood glenn is in haha.

C2 every day of the week glenn.

And it would work, just potentially dangerous - unless it was a 17th ed board and the interconnected circuits were on different RCD's.

Now, calm your passions glenn :p
 
Ok to start with it is against the regs as has been pointed out, then if the line and neutral are on different RCD's they won't hold as they will be out of balance. And non-technically it doesn't make much sens.

Code? Umm, C2 I would think?
 
I see what mood glenn is in haha.

C2 every day of the week glenn.

And it would work, just potentially dangerous - unless it was a 17th ed board and the interconnected circuits were on different RCD's.

Now, calm your passions glenn :p
the concept here Mark was that strops could answer the question...
never mind:biggrin:
 
I can honestly say that I posted my answer before I saw Mark's anwer. And I thought C2 then cheated slightly by looking it up which took extra time. By that time he had posted!

As an apprentice I would have no shame in admitting I don't know something.

Until I came on here I didn't know borrowed neutrals existed, so I've learnt something!
 
Glenn, do you fancy asking the OP if us two can go around and have a look? Bet we could sort this out in less than 2 hours, including testing and cert!
 
Glenn, do you fancy asking the OP if us two can go around and have a look? Bet we could sort this out in less than 2 hours, including testing and cert!

I suspect you my not get an answer.. fink we have scarred him away on this occasion
 
Aye, the OP wont be back lol.

He'll crack on with the work, not certify it and the client will be none the wiser...another day in sparky land then.
 