shnabz

Where the hell is the answer to the following question in BS 7671:

The required current carrying capacity of a three-phase circuit conductor I[SUB]z [/SUB] is 26A. From the correct table, the minimum size of three single-core thermoplastic covered, heavy duty MICC cables, installed flat on a perforated cable tray and spaced by two cable diameters is
A.1.0mm2
B.1.5mm2
C.2.5mm2

D.4.0mm2
 
table 4G1A in the BGB. might be differeny in BYB.
 
That's a good point, none of the above answers are correct as 1H6 is the smallest listed
 