Not trying to nit pick....but.
Table 41.3 max Zs etc are at 100% values whereas GN3 table B.4 show 80% values but some of the values in GN3 are not even close to being rounded up.
For example a type C 32 amp bsen60898 = 0.72 in regs book
GN3 =0.62 for the same device.
but 0.72x 0.8=0.58 at best ....... thats not really close to being 0.62.
Any clarity?
Table 41.3 max Zs etc are at 100% values whereas GN3 table B.4 show 80% values but some of the values in GN3 are not even close to being rounded up.
For example a type C 32 amp bsen60898 = 0.72 in regs book
GN3 =0.62 for the same device.
but 0.72x 0.8=0.58 at best ....... thats not really close to being 0.62.
Any clarity?