Not trying to nit pick....but.
Table 41.3 max Zs etc are at 100% values whereas GN3 table B.4 show 80% values but some of the values in GN3 are not even close to being rounded up.
For example a type C 32 amp bsen60898 = 0.72 in regs book
GN3 =0.62 for the same device.

but 0.72x 0.8=0.58 at best ....... thats not really close to being 0.62.

Any clarity?
 
Hi Silver Surfer, The values tabulated in GN3 and OSG are not calculated by the simple rule of thumb. They are calculated using a more complicated method (see GN3 B1 and EIDG) that compensates for conductor temperature and yields a more accurate result. These tables are useful in situations where the rule of thumb yields marginal non-compliance, often referring to the GN3 or OSG tables, reveals that by the more accurate method of calculation the device does actually comply.
 
Last edited by a moderator:
Not trying to nit pick....but.
Table 41.3 max Zs etc are at 100% values whereas GN3 table B.4 show 80% values but some of the values in GN3 are not even close to being rounded up.
For example a type C 32 amp bsen60898 = 0.72 in regs book
GN3 =0.62 for the same device.

but 0.72x 0.8=0.58 at best ....... thats not really close to being 0.62.

Any clarity?

Yes your not looking close enough.

Gn3 for a 32 amp states .58, your looking at 30 amp.

Regards Chris
 

Reply to BS7671 V GN3 MAX Zs Values in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi new member here looking for a bit of advice. I recently undertook a condition report of a building where the measured Zs at the distribution...
Replies
20
Views
5K
Hi all, Just wondering if anyone can shed some light on the max zs values in the OSG, they don’t seem to follow the 1.25 divisor stated in the...
Replies
10
Views
8K
SORRY FOR LONG POST. So i have my 2391-52 multiple questions coming up on Friday 13th, ( yeh i know) and was giving some things to study over by...
Replies
4
Views
2K
Hi All, Thank you for welcoming to this forums I just want to clarify that the Value I need to enter 100% or 80% in the last column "Maximum Zs...
Replies
32
Views
10K
Hi all, Why is there no max Zs value for a 45A type B breaker in table 41.3 of 18th edition? What value should be used as max value on schedule of...
Replies
13
Views
9K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock