Hi All,
Thank you for welcoming to this forums

I just want to clarify that the Value I need to enter 100% or 80% in the last column "Maximum Zs Permitted by BS7671"
is it 80% from the table 41.3 from 18th Edition Regs - Page 62 or the value from Pocket Guide 18

Thank you
Loges
 

Attachments

Aico Carbon Monoxide Detectors
This official sponsor may provide discounts for members

Paignton pete

-
Arms
Esteemed
I was taught to put the 80% down. And that’s what I’ve always done.

This was discussed in a previous thread and some said 100% others 80%.

I don’t think it really matters as long as you know which your using on the comparison to the actual Zs read and you know what your doing.
 
D

Deleted member 9648

If a 30ma RCD is incorporated along with the overcurrent device then technically the maximum permitted Zs is 1667 ohms, but you almost never see this applied to TN systems, most incorrectly use the max Zs for the OCPD.
411.4.5.......411.4.204 and table 41.5 apply to TN systems.
 

Strima

-
Arms
Esteemed
If the certificate asks for "Maximum Zs Permitted by BS7671" then you put down the 100% figure from the book as that is what it is asking for.
 
D

Deleted member 26818

As Strima says, you put down the value found in BS7671.
This is so the customer gets confused when the measured value is less but it still fails.
 
Last edited by a moderator:

telectrix

-
Mentor
Arms
Esteemed
As Strima says, you put down the value found in BS7671.
This is so the customer gets confused when the measured value is less but it still fails.
but then you confuse them even more by telling them it's oK, with RCD it's 1667.
 

UNG

-
Mentor
Arms
For me you should use the 80% value

The maximum permitted Zs value is 80% of the maximum allowed value

As the certs asking for the maximum permitted value then the 80% value should be used
 

telectrix

-
Mentor
Arms
Esteemed
BUT 80% is not max. it's corrected assuming cable will be fully loaded and at 70 deg.C. this will never happen. cables will be at least 30% overloaded and breaker will trip long before that temp. is reached (assuming circuit has been designed in compliance with 7671). tin hat on.
 

Paignton pete

-
Arms
Esteemed
BUT 80% is not max. it's corrected assuming cable will be fully loaded and at 70 deg.C. this will never happen. cables will be at least 30% overloaded and breaker will trip long before that temp. is reached (assuming circuit has been designed in compliance with 7671). tin hat on.
Absolutely agree. I don’t understand why we even use 80%. It is overkill.
I think 90-95% would be adequate just to allow for design flaws and anomalies.

However the Cmin factor that gives 95%. So I recon that should be sufficient.

Obviously there may be very good reasons 80% is used. Maybe a figure plucked out of the air. I don’t know. Any ideas?
 