Discuss Weird Question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Bear
SORRY FOR LONG POST.
So i have my 2391-52 multiple questions coming up on Friday 13th, ( yeh i know) and was giving some things to study over by other engineers in my group and came across this question and i have the answers here too but i think its wrong? or i don't understand it correctly!
The calculations i did where: - 6.44 x 15/1000=0.0966ohms Then i did:- 0.0966+0.51= 0.6066, Rounded to 0.61ohms
Did this for them all.
A domestic dwelling (2-storey) is supplied with a TN-S systems of earthing with a declared Ze = 0.51 ohms. Protective devices are to BSEN60898 type B.
Circuits are wired in pvc/pvc flat cable. Circuits comprise of;
40A circuit -Cooker wired in 10/4mm2, circuit length is 15m
40A circuit -Shower wired in 6/2.5mm2, circuit length is 20m
32A Shed supply sub-main wired in 4/2.5mm2, circuit length is 59m
A1 ring wired in 2.5/1.5mm2, circuit length is 24m
A3 radial wired in 2.5/1.5mm2, circuit length is 11m
6A circuit -Lighting wired in 1.5/1mm2, circuit length is 16m
Calculate the expected Zs values for each circuit.
Verify these results would not exceed maximum ‘measured’ Zs values as shown in BS7671:2018
ANSWERS
Use Table I1 in O.S.G (milli-OHM) x length
(6.44 x 15)/1000=0.61 ohms (r1+r2). So Zs = 0.51+0.61= 1.12 ohms.
Fixed equipment, over 32A, so 5sec disconnection time required. Max (measured) Zs limit is 0.88 ohms (fail)
(10.49 x 20)/1000=0.72 ohms (r1+r2). So Zs = 0.51+0.72= 1.23 ohms.
(12.02 x 59)/1000=1.22 ohms (r1+r2). So Zs = 0.51+1.22= 1.73 ohms
Distribution circuit, so 5sec disconnection time required. Max (measured) Zs limit is 1.1 ohms (fail)
(19.51 x 24)/1000=0.47 ohms, now divide by 4 to find (r1+r2) because it is a RING, so 0.47/4 = 0.12 ohms, So Zs = 0.51+0.12= 0.63 ohms.
Sockets, not exceeding 63A, so 0.4sec disconnection time required. Max (measured) Zs limit is 1.1 ohms (pass)
(19.51 x 24)/1000=0.72 ohms (r1+r2). So Zs = 0.51+0.72= 1.23 ohms
Sockets, not exceeding 63A, so 0.4sec disconnection time required. Max (measured) Zs limit is 1.75 ohms (pass)
(30.2 x 15)/1000=0.61 ohms (r1+r2). So Zs = 0.51+0.61= 1.12 ohms
Fixed equipment, not exceeding 32A, so 0.4sec disconnection time required. Max (measured) Zs limit is 5.87 ohms (pass)
In the answers it looks like they’ve added Ze twice in every part. Your answer to the first question makes more sense
“(6.44 x 15)/1000=0.61 ohms (r1+r2)” the maths for this part just doesn’t work unless you add 0.51 (Ze) to the result, which for some bizarre reason they then do again.
Wherever you got those sample questions from, the calculations in the answers are incorrect.
Edit, beaten to it by @dodger421!
Edit again: they haven't just added the Ze twice on all of the calculations, they have completely ballsed it up!
Reply to Weird Question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
hi in college and watched some YouTube videos and read up on things I think I got the right formula but I'm not sure. Zsc= Zesc(or Zdbsc) +...
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...