Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained was 0.97 Ohms and 27Amps Pfc.
CH]
Assuming Uo of 230V then calculated PFC is Uo/Ze = 230/0.97 = 237A not 27A, a factor 10 different. Is 27A a typo and you meant to write 237A?
 
The two supplies are also sharing the same neutral .
For a split phase or two of three phase supply the neutral never carries a residual current of more than that of the highest line's current.

Is the remark you made directed at the fact that the shared neutral conductor in the cable to the cottages is fed by two switched neutrals?
 
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Scotland
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Cottage supplied by 16mm SWA 300+ yards! Trying to resolve a high Ze reading
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
22

Advert

Thread statistics

Created
RobertLow,
Last reply from
ukiri,
Replies
22
Views
3,570

Advert