AJB Temple
DIY
CONCLUSION
(Couldn't see how to edit title)
It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres away from the socket and down a brick built chamber around 4 or 5 feet deep. It's fed from various storm drains and then pumped out to a large pond which then drains into a stream. Clean water only. But lots of it in a storm and it's a sunken terrace that can flood. The cable to the pump runs through a metal conduit (you can see where I am going here) underground just below the paving level but above the normal activation point for the float switch. The cable is terminated in a new 13amp rubber plug which goes into a new and good quality outdoor socket fitted by me. Put the megger on the socket and it tests fine. No water ingress either.
Took the plug off and pulled the wire through with a feeder twine. Cable from pump has been nibbled by something, probably voles (we have lots) about 1 meter into the pipe. They must have been determined as pipe is only about an inch diameter at most and had a thick rubber cable in it. Degraded insulation was shorting out on the pipe I expect. Cable replaced with new rubberised cable and pump tested. Runs fine, no trips. Plugged both ends of the cable pipe with silicone.
The lesson for me is that I assumed I was at fault and spent ages going over my work trying to find a non existent error. It was only when one of you guys (thanks very much PC1966) mentioned a fridge being connected, that I remembered the outdoor pump which I had forgotten was on that ring circuit (daft design - but I didn't do it). Pure coincidence that the pump feed shorting occurred just when I was working on something on the same circuit.
(Couldn't see how to edit title)
It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres away from the socket and down a brick built chamber around 4 or 5 feet deep. It's fed from various storm drains and then pumped out to a large pond which then drains into a stream. Clean water only. But lots of it in a storm and it's a sunken terrace that can flood. The cable to the pump runs through a metal conduit (you can see where I am going here) underground just below the paving level but above the normal activation point for the float switch. The cable is terminated in a new 13amp rubber plug which goes into a new and good quality outdoor socket fitted by me. Put the megger on the socket and it tests fine. No water ingress either.
Took the plug off and pulled the wire through with a feeder twine. Cable from pump has been nibbled by something, probably voles (we have lots) about 1 meter into the pipe. They must have been determined as pipe is only about an inch diameter at most and had a thick rubber cable in it. Degraded insulation was shorting out on the pipe I expect. Cable replaced with new rubberised cable and pump tested. Runs fine, no trips. Plugged both ends of the cable pipe with silicone.
The lesson for me is that I assumed I was at fault and spent ages going over my work trying to find a non existent error. It was only when one of you guys (thanks very much PC1966) mentioned a fridge being connected, that I remembered the outdoor pump which I had forgotten was on that ring circuit (daft design - but I didn't do it). Pure coincidence that the pump feed shorting occurred just when I was working on something on the same circuit.
Last edited: