Hi there,
I'm Currently doing my design calcs for my college project and doing the actual Zs calculation.
Formula is Zs= Ze (or Zdb) + (R1+R2)
Then for (R1+R2) you find the (R1 +R2) per metre value in the On site guide appendix i - i1 , which for me line and cpc are both 1mm so its 36.20 . I then need to multiply this by the length of the circuit which is 30m and multiply by the factor for maximum operating temperature then divide this by 1000 to convert to ohms . And in the table i3 it gives u 2 options of conductor installation: Not incorporated with cable and not bunched or Incorporated in a cable or bunched. And I'm using 1mm single core cables for this circuit which will be installed in the same conduit together so I'm pretty sure that this would be classed as bunched but I wanted to double check.
 
Read up on the definitions of conductors, then circuits. Then double check what bunching is defined as - and the answer will be apparent PLUS you’ll probably end up learning something else as well along the way. Oh…… and well done on fully stepping through your maths!
 
Upvote 0

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Sheffield
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
If you have 3 single core cables in conduit for a singular circuit would this be classed as bunched?
Prefix
N/A
Forum
Electrician Courses : Electrical Quals
Start date
Last reply date
Replies
1
Unsolved
--

Advert

Thread statistics

Created
WilliamAtkin,
Last reply from
Rockingit,
Replies
1
Views
1,972

Advert

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.