Discuss Updating cable calc spreadsheet in the UK Electrical Forum area at ElectriciansForums.net
Hi All,
Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop figures but I'm just looking for some clarity on figures.
For 3-core 16mmsq SWA, single phase, I'm looking at table 4D4B in BS7671 and it states:
  • Two-core cable, single-phase AC - 2.8 mV/A/m
  • Three or four-core cable, three-phase AC - 2.4 mW/A/m
What would the correct value be in the context of the above cable?
Also for Zs and calculating R1+R2 for same, the on-site guide says in table I1 that for 16mmsq, copper conductor R/m is 2.3 Ohms. For ducted cable, should this be multiplied by 1.2 (Table I3), to give value of 2.76 Ohms?
Any guidance is much appreciated.
If it is single phase then 2.8 mV/A/m applied to your nominal 230V L-N for both 2C and 3C cable (when 3rd core is used as CPC).
If it is three-phase then use 2.4 mV/A/m applied to your nominal 400V L-L for both 3C (3L such as delta motor load), and also 4C (3L+N) provided you have reasonable balance between phases (so your N drop is small).
Table I1 is for the cable when cold = 20C, other values are for cable hot which is usually assumed to be 70C for PVC insulation.
For cables running 90C with XLPE the drop is more as hotter copper means higher R, but few accessories are happy at tat sort of rating so you need to think twice before adopting that CCC limit.
Why would you choose the 3 core table if its single phase, surely you dont count the earth or spare core when doing the calculations.
You might need a 10mm Cu CPC for PME bonding, or to meet disconnection times if armour R2 too high.
How can a 16mm SWA have a resistance of 2.3 ohms/M. You might as well use some string.
They probably meant Ohm/km but I would put mOhm/m and use the omega letter if I could find a simple way to type its code in...
Thanks all, for the assistance. It's much appreciated.
The third core is CPC but looking at previous versions of the .xls shows some of the values are taken from the 3/4 core 3-phase table, so it's been throwing me a bit. Seems to be some difference on opinion on th correct Vd table.
With regards to 90⁰/XLPE, there seems to be some clarifications required on device compatibility in the regs for this so will stick to 70⁰ as a fail safe.
Thanks again.
70C is a safe assumption.
Where 90C helps are cases of a cable going through a hot area (e.g. near hot water pipes), or a region of high thermal insulation, so the ends are OK temperature-wise (70C or below) but the middle needs the extra capacity.
Thanks mate. The spreadsheet is typically used for street lighting design.
Reply to Updating cable calc spreadsheet in the UK Electrical Forum area at ElectriciansForums.net
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
Hi everyone, I'm new here and was wondering if someone could help to get my college project calculations right. I'm about to start my 2nd year in...
7K
Its been long since I was in college doing cable calcs and obeing onsite as I've studied a completely different course at university, I understand...
After my last post and having and having to re-learn some stuff can someone check and advise on a few things. Sorry if this is wrong don't hate...