Its been long since I was in college doing cable calcs and obeing onsite as I've studied a completely different course at university, I understand de-rating factors but need some clarifying up to brush up.

If I need a 600A supply which can be split 200A each phase. and being supplied via SWA underground over a distance of 200m at a depth of 0.8 to a sub dis board.

When doing cable calcs do I use 200A or 600A?
And when reading cable datasheets for 3 phase reference method d - 1|thee or 1 four-core cable three-phase AC , does the data in the table refer to each phase ie. as 1mm2 - 21A per phase or 7A.
Bit of a stupid question

Thanks for your help.
 
Another thing to consider is the voltage drop over 200m.
 
Hi - there are no stupid questions, but my thought is you should be able to work this one out from first principles. Have you got BS7671 to hand? In your example what is single phase current carrying capacity for 1mm? Then for 3 phases at 1mm?
 
Cable calculations and data tables are based on the actual current in each conductor. You happen to have single-phase loads spread over the three phases of a 200A 3-phase, 4-wire circuit. If instead you chose to supply the loads from a single-phase circuit, the conductor current would then be 600A and that would be the figure to use in the calculations.
 
Cable calculations and data tables are based on the actual current in each conductor. You happen to have single-phase loads spread over the three phases of a 200A 3-phase, 4-wire circuit. If instead you chose to supply the loads from a single-phase circuit, the conductor current would then be 600A and that would be the figure to use in the calculations.
Thanks , think i just had a brain meltdown yesterday
 

Reply to Cable calcs 3 phase in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all Just doing some cable calcs for a shepards hut site, the site has an incoming supply of 2 x 250a single phase supplys, was hoping to...
Replies
5
Views
878
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
584
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock