Yes either metal or plastic is fine but additional precautions must be taken if you opt for metal. IMO in the Op’s Situation I would of used an IP rated plastic board like I linked to. I don’t understand really why you would want to introduce a potential that wouldn’t exist if a plastic board was installed...especially on a building site where things regularly get knocked/pulled about. Maybe the difference is actually understanding and going above and beyond the Bare minimum.Not again,a metal DB fine too....
Probability of the fault scenario ,quite small,using appropriate cleats etc,would minimise this,still a metal DB for me.Hi all
It is TT so at the meter position use a 300ma to 500ma RCD linked to a SPD in a plastic enclosure. DO NOT USE METAL AS THERE IS NO RESETABLE SAFETY CUTOUT BETWEEN THIS AND THE SUPPLY!! Any fault prior to the incoming RCD with blow the Supply Company fuse resulting in site black-out and a call out charge, not to mention blue language.
Earthing at this point must be to a dedicated earth spike and make sure the earth is good.
The SPD is necessary as if there is a lightning strike on the TT supply anybody working on rebar gets fried!
The choice of DBs after this is up to the installer.