Hi all. Thanks for the replies. Should have added, the concrete slab is 3.6m above ffl. The cables are run around the edge of rooms, stabbing out to light fittings.

I’ve tried explaining the regs to the BI, but to no avail. Even the client thinks he’s just being bloody minded.

Unfortunately, I think we are all going to have a lot more of this and as with all regulation changes, our costs are going to increase.

On a bright note, it’s a one off job south of London, 50 miles from home. So I won’t have to deal with him again

Thanks again for the input
 
It may have been in the specification of the job & not just the regs, whatever way the inspector may have said it.
 
My understanding, is that the Regulations require us to prevent premature collapse of cables.
For many years now, I have been using metal ties about a meter apart, or every third tie.

I am not aware of there being a requirement for every fixing to be metal.
 
Is that all he’s got to worry about,looking @ some of the sparkies out there,they ought to have metal ties round their feet,stop them working ha ha
 
521.10.202 Wiring systems shall be supported such that they will not be liable to premature collapse in the event
of a fire.
NOTE 1: Wiring systems hanging across access or egress routes may hinder evacuation and firefighting activities.
NOTE 2: Cables installed in or on steel cable containment systems are deemed to meet the requirements of this regulation.
NOTE 3: This regulation precludes, for example, the use of non-metallic cable clips or cable ties as the sole means of support
where cables are clipped direct to exposed surfaces or suspended under cable tray, and the use of non-metallic cable
trunking as the sole means of support of the cables therein.
NOTE 4: Suitably spaced steel or copper clips, saddles or ties are examples that will meet the requirements of this regulation.
 
521.10.202 Wiring systems shall be supported such that they will not be liable to premature collapse in the event
of a fire.
NOTE 1: Wiring systems hanging across access or egress routes may hinder evacuation and firefighting activities.
NOTE 2: Cables installed in or on steel cable containment systems are deemed to meet the requirements of this regulation.
NOTE 3: This regulation precludes, for example, the use of non-metallic cable clips or cable ties as the sole means of support
where cables are clipped direct to exposed surfaces or suspended under cable tray, and the use of non-metallic cable
trunking as the sole means of support of the cables therein.
NOTE 4: Suitably spaced steel or copper clips, saddles or ties are examples that will meet the requirements of this regulation.

Which is exactly what I’ve told him. He states that “suitably spaced” means with gaps as per regs and mustn’t be plastic.

I know I’m right, but it is difficult to argue with someone that has a little knowledge and won’t listen
 
Well If he insisted that was the case, I would get from him in writing his insistence at alteration of an installation. Also his reasoning and suggest the installation must be certified by him as he is materially altering a circuit??? Ok maybe not but I would get him to sign and state reasons for altering the installation.
 