Tenant reported that his fuse box caught fire. I found this stove circuit pullout. This unit was built in the 60s wired in aluminum but I found no corrosion and no indication of foil or other foreign material in the box.. The fuses are Bussman NON-35 Amp. Probably the original fuse from the 50s. I installed a new breaker box.
Never seen or heard of this. Any suggestion what happened?
16626495818932274062019981283442.jpg
 
Most likely cause is that high resistance had developed at one of the fuse end caps, which began to arc and burn material away until enough heat was being generated to scorch the phenolic moulding. There is a notch in the end cap that suggests it was the fuse element arcing to the end cap, although I suspect the initiating failure was more likely to be high resistance to the pull-out contact.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Macon, Ga
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United States of America
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Bussman NON-35 fuse fire?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
1
Unsolved
--

Advert

Thread statistics

Created
gashmore,
Last reply from
Lucien Nunes,
Replies
1
Views
1,211

Advert

Back
Top