Looking at putting a lathe into a workshop.. 16A, 3 phase, a run of 19metres at approx 35 degrees.

Also, a 3 phase, arc welder which I was going to put into a 32A socket outlet. 7 metre run, again at 35 degrees.

Can someone help with how I would complete a cable calculation for either?! Completely confused with three phase systems!

Cable will be run on perforated tray in an empty (non insulated) ceiling void.
 
Looking at putting a lathe into a workshop.. 16A, 3 phase, a run of 19metres at approx 35 degrees.

Also, a 3 phase, arc welder which I was going to put into a 32A socket outlet. 7 metre run, again at 35 degrees.

Can someone help with how I would complete a cable calculation for either?! Completely confused with three phase systems!

Cable will be run on perforated tray in an empty (non insulated) ceiling void.

Hi Emily.
Is this a homework question?
Tell us what you think. Show us your calcs and we are always happy to help.
We don't like just telling people the answer, as they don't learn anything.
 
Not a homework question, been given it by my boss and told to 'figure it out'.. I can complete single phase.. but unsure of how to calculate the design current at the start for 3 phase? I know the rest thing with correction factors etc
 
. but unsure of how to calculate the design current at the start for 3 phase?

You don't need to calculate the current.... do you?
You have a 16A supply and a 32A supply. I presume the breaker for the arc welder will be 32A? You just say you are using a 32A socket outlet.
So all you need to do is select the correct size cables.
Or am I missing something?
 
Its been a while but here goes:

Ib = Power (W) / Root 3 x Uo (V) x p.f

Where:

Ib = Design Current
Uo = Nominal Voltage (400V)
p.f. = Power Factor (Usually motors)

Then you select Device rating, In

Then you calculate Iz by applying correction factors : Iz = In/Cf

Ib < In < Iz

This is then used to size cable for current carrying capacity. Using this cable information you calculate the expected voltage drop:

VD(V) = mV/A/m x Ib x l
1000

This is where you would use your design current, but if you used In instead it would give the maximum expected volt drop for that circuit with the selected cable type.

Please be kind if i'm wrong with what I have posted as I believe that everyday is a school day.
 
It equal to or greater than
In/ ca cc cg ci

Without overload
Ib/ ca cc cv ci

Iz=It ca cc cg ci

And basically any other correction factor such as underground soil resistivity depth and such
 
what's soil resistivity got to do with it. you don't send current through soil.(hopefully)
 
what's soil resistivity got to do with it. you don't send current through soil.(hopefully)
Just mentioning different correction factors involved in cable calcs and if buried in soil it's one of them.
Obviously some aren't always required :)
 