Cable Calculations?!

Soil resistivity has no bearing on cable calculations, it is only used in calculations for earth electrodes.
 
Cables buried in the ground – soil thermal resistivity (Cs)
The current-carrying capacities tabulated for cables in the ground are based upon a soil thermal resistivity of 2.5K.m/W and are intended to be applied to cables laid in and around buildings, i.e. disturbed soil.

In locations where the effective soil thermal resistivity is higher than 2.5K.m/W, an appropriate reduction in current-carrying capacity should be made. Rating factors for soil thermal resistivities other than 2.5K.m/W are given in Table 4B3
 
Cs is the soil thermal resistivity, this is a completely different thing to soil resistivity.
Resistivity (rho) is the electrical resistance per unit area of a material.
Thermal resistivity is the reciprocal of the thermal resistance of a material.

These two physical properties are very different things,
 
Cs is the soil thermal resistivity, this is a completely different thing to soil resistivity.
Resistivity (rho) is the electrical resistance per unit area of a material.
Thermal resistivity is the reciprocal of the thermal resistance of a material.

These two physical properties are very different things,
Dave I was mentioning a correction factor based on cables in soil cs which you say doesn't exist! And you've tried to turn it round
 
Now now children.... play nice.

I would like to point out that I did mention correction factors in my original post. But as you've elaborated on that a bit more than my generic terminology of CF are correction factors, so be it.

And not one to really sit on a fence, i think dave is right ;)
 
Cs is the soil thermal resistivity, this is a completely different thing to soil resistivity.
Resistivity (rho) is the electrical resistance per unit area of a material.
Thermal resistivity is the reciprocal of the thermal resistance of a material.

These two physical properties are very different things,

Jesus you know full well what he meant. What is wrong with you?
 
Now now children.... play nice.

I would like to point out that I did mention correction factors in my original post. But as you've elaborated on that a bit more than my generic terminology of CF are correction factors, so be it.

And not one to really sit on a fence, i think dave is right ;)
Right about what?
 