Soil resistivity has no bearing on cable calculations, it is only used in calculations for earth electrodes.
Think you find it does cs is its symbolSoil resistivity has no bearing on cable calculations, it is only used in calculations for earth electrodes.
Think you find it does
Dave I was mentioning a correction factor based on cables in soil cs which you say doesn't exist! And you've tried to turn it roundCs is the soil thermal resistivity, this is a completely different thing to soil resistivity.
Resistivity (rho) is the electrical resistance per unit area of a material.
Thermal resistivity is the reciprocal of the thermal resistance of a material.
These two physical properties are very different things,
Dave I was mentioning a correction factor based on cables in soil cs which you say doesn't exist! And you've tried to turn it round
What all because I missed the word thermal nice tryyou stated that soil resistivity affects cable calculations, it does not.
What all because I missed the word thermal nice try

Cs is the soil thermal resistivity, this is a completely different thing to soil resistivity.
Resistivity (rho) is the electrical resistance per unit area of a material.
Thermal resistivity is the reciprocal of the thermal resistance of a material.
These two physical properties are very different things,
Right about what?Now now children.... play nice.
I would like to point out that I did mention correction factors in my original post. But as you've elaborated on that a bit more than my generic terminology of CF are correction factors, so be it.
And not one to really sit on a fence, i think dave is right![]()